Corner Rad

Posted on 16/12/2012 2:20pm
barney97

when first installed and bled only half the rad heated, now dosnt heat at all Can you advise on what I need to do to resolve.

Thanks

Barney


1 Replies
  • AdminUser
    Commented on 16/12/2012 2:20pm

    Barney,
    I assume we are talking about an Iguana Corner. If so, then it is almost certainly air trapped in the radiator. Air gets trapped in the elbow that connect the triangular waterways.
    This will need to be vented as per the instructions found at:
    www.jaga.co.uk/filedownload/areas/jaga/content/documents/productfamilies/iguana/IguanaWallAirVentInstr.pdf

    An alternative method would be to hit the radiator with something such as a rubber mallet to dislodge the air. This will obviously need venting, and possibly need to be vented from the next radiator along the line.
    You may need to carry this out several times.

    Regards

    Andy W
    Jaga UK